Question 6057 of 844 · Washington 01 Journey Level Electrician Exam
Which location is classified as a wet location?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6057
- A: Underground or in concrete slabs in direct contact with the earth
Explanation
Wet locations include installations underground, in concrete slabs or masonry in direct contact with the earth, subject to saturation, or unprotected and exposed to weather. Covered porches and basements are typically damp locations. See Article 100.
More questions: Wiring Methods, Conductors and Boxes
- 6058In NEC 2020 and 2023, aluminum, copper-clad aluminum, or copper conductors may be run in parallel only when they are
- 6063Which use of a flexible cord is prohibited?
- 6066Which location permits Type NM cable?
- 6067In an attic reached only by a scuttle hole, NM cable run across the top of joists must be protected by guard strips within what distance of the scuttle hole?
- 6068In an unfinished basement, NM cable run at angles to joists must be run through bored holes or on running boards if it is smaller than
- 6069The ampacity of NM cable conductors is generally determined using which temperature column?