Question 6056 of 844 · Washington 01 Journey Level Electrician Exam
XHHW insulation, without the -2 suffix, is rated 90 C in dry and damp locations and what in wet locations?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6056
- D: 75 C
Explanation
XHHW is a cross-linked polymer insulation rated 90 C dry or damp and 75 C wet. XHHW-2 is rated 90 C wet and dry. See the conductor application table in Article 310.