Question 6059 of 1033 · Washington 01 Journey Level Electrician Exam
Which requirement applies to each phase of a set of paralleled conductors?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6059
- C: Same length, material, size, insulation, and termination
Explanation
Paralleled conductors in each phase, polarity, or grounded conductor set must be the same length, same conductor material, same size, same insulation type, and terminated the same way so the current divides equally. See 310.10(H) in NEC 2020 and 310.10(G) in NEC 2023 and 2026.
More questions: Wiring Methods, Conductors and Boxes