Question 8018 of 966 · Washington 01 Journey Level Electrician Exam
An inverse time breaker sized at 250 percent will not carry the starting current of a motor with a full-load current under 100 A. What is the maximum it may be increased to?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8018
- C: 400 percent of full-load current
Explanation
Exception No. 2 to 430.52(C)(1) lets the rating of an inverse time breaker be increased but not beyond 400 percent for full-load currents of 100 A or less, and 300 percent above 100 A. Dual-element fuses may go to 225 percent under the same exception.
More questions: Motors, HVAC, Generators and Transformers
- 8020Where must a motor disconnecting means be located in relation to the motor and driven machinery?
- 8021What does the NEC mean when it says equipment is in sight from other equipment?
- 8022What is the minimum ampere rating of a motor disconnecting means for a motor rated 1000 volts or less?
- 8023A motor disconnect switch for a 10 hp motor must be rated in which unit?
- 8024How many conductors must a motor disconnecting means open?
- 8025What must a motor disconnecting means clearly indicate?