Which installation is generally outside the scope of the NEC?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1102
- C: Utility-owned generation and distribution equipment under the utility's exclusive control
Explanation
90.2 lists installations under the exclusive control of an electric utility for generation, transmission and distribution as not covered by the Code. Premises wiring on the load side of the service point is covered.