What is the demand load for one 10.5 kW household range under the NEC 2020 or 2023?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12120
- D: 8 kW
Explanation
A single range over 8.75 kW and not over 12 kW takes 8 kW from Column C (Table 220.55).
More questions: Load Calculations