Question 12121 of 966 · Washington 01 Journey Level Electrician Exam
Using the NEC 2020 or 2023 standard method, what is the demand load for one 17 kW range?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12121
- A: 10 kW
Explanation
Column C rises 5 % for each kW above 12 (Table 220.55, Note 1). 17 kW is 5 kW over, so 8 kW x 1.25 = 10 kW.
More questions: Load Calculations
- 12122Nine 13 kW ranges serve an apartment building. Under the NEC 2020 or 2023, what is the range demand load?
- 12021Using the standard method under the NEC 2020/2023, what general lighting load must be included in the service calculation for a one-family dwelling with 2,400 ft2 of livable floor area?
- 12022A 2,000 ft2 dwelling has the minimum two small-appliance circuits and one laundry circuit. Under the NEC 2020/2023 standard method, what is the demand load for general lighting, small-appliance and laundry loads combined?
- 12023A 3,200 ft2 one-family dwelling has three 20 A small-appliance circuits and one laundry circuit. Under the NEC 2020/2023 standard method, what is the net demand load for these loads plus general lighting?
- 12024Under the NEC 2020/2023 standard method, what is the demand load for general lighting, two small-appliance circuits and one laundry circuit in a 4,500 ft2 dwelling?
- 12025Optional method (NEC 2020/2023): a 2,000 ft2 dwelling has two small-appliance circuits, one laundry circuit, a 12 kW range, a 5 kW dryer, a 1,200 VA dishwasher and a 4,500 W water heater. What is the calculated general load (heating and AC excluded)?