Question 4092 of 1033 · Washington 01 Journey Level Electrician Exam
What is the minimum branch circuit rating for a household range rated 8 3/4 kW or more?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4092
- B: 40 amperes
Explanation
210.19 sets 40 amperes as the minimum branch circuit rating for household ranges of 8 3/4 kW or more. The actual size is based on the demand load for the range.
More questions: Branch Circuits, GFCI and AFCI
- 4093Tap conductors from a 50-ampere range branch circuit to a wall-mounted oven must have an ampacity of at least what value?
- 4094A multiwire branch circuit supplies receptacles in a dwelling. What does the NEC require at the point where the branch circuit originates?
- 4095A multiwire branch circuit in general may supply only which type of load?
- 4096How must the conductors of a multiwire branch circuit be identified in a panelboard?
- 4097In a 120/240-volt, 3-wire multiwire branch circuit, why must the two ungrounded conductors be connected to opposite lines?
- 4098In a dwelling living room, what may substitute for the required wall-switch-controlled lighting outlet?