Tap conductors from a 50-ampere range branch circuit to a wall-mounted oven must have an ampacity of at least what value?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4093
- D: 20 amperes
Explanation
210.19 permits tap conductors from a 50-ampere branch circuit supplying ranges, wall-mounted ovens and counter-mounted cooking units if they have an ampacity of at least 20 amperes. They must be sufficient for the load and not longer than needed for servicing.